Element 1 Question 1-18C4
C1C18: Equipment Faults
What would be an indication of a malfunction on a GMDSS station with a 24 VDC battery system?
- A constant 30 volt reading on the GMDSS console voltmeter. (correct answer)
- After testing the station on battery power, the ammeter reading indicates a high rate of charge that then declines.
- After testing the station on battery power, a voltmeter reading of 30 volts for brief period followed by a steady 26 volt reading.
- None of the above.
Correct answer: A, A constant 30 volt reading on the GMDSS console voltmeter.
Explanation
A healthy 24 V lead-acid bank charges above its nominal voltage and then settles to a float of about 26–27 V. A reading stuck at 30 V means the charger's regulator has failed and the charger keeps overcharging the batteries, which makes them gas, lose water and get damaged. A high charge current that tapers off, or a brief high voltage that drops to a steady float, is normal recovery after a battery test.
Why the other answers are wrong
- B, After testing the station on battery power, the ammeter reading indicates a high rate of charge that then declines.: This is normal. After a battery test the charger first replaces the used charge at a high rate, and the current falls as the battery fills.
- C, After testing the station on battery power, a voltmeter reading of 30 volts for brief period followed by a steady 26 volt reading.: This is also normal: a short high charging voltage followed by a steady float of about 26 V is how a working charger brings a 24 V bank back up.
- D, None of the above.: A constant 30 V reading does show a fault (the charger is overcharging), so it is wrong to say none of the choices is a malfunction.