How should shielding be grounded on an NMEA data line?
- Unterminated at both ends.
- Terminated to ground at the talker and unterminated at the listener. (correct answer)
- Unterminated at the talker and terminated at the listener.
- Terminated at both the talker and listener.
Correct answer: B, Terminated to ground at the talker and unterminated at the listener.
Explanation
Ground the shield of an NMEA data cable at one end only, the talker (source) end, and leave it unconnected at the listener. If you ground both ends, any difference in ground potential between the two devices drives current along the shield. That ground loop puts noise into the data. With one ground point, the shield still drains interference with no loop current.
Why the other answers are wrong
- A, Unterminated at both ends.: If the shield isn't grounded at either end, picked-up interference has no path to ground, so the shield gives almost no protection.
- C, Unterminated at the talker and terminated at the listener.: This grounds the wrong end. The standard practice is to ground the shield at the talker, the signal source, and leave the listener end open.
- D, Terminated at both the talker and listener.: Grounding both ends creates a ground loop. Current from potential differences then flows in the shield and adds noise to the data.