General Question G0B11
G0B: Station safety: electrical shock, grounding, fusing, interlocks, and wiring; antenna and tower safety
Which of the following is required for lightning protection ground rods?
- They must be bonded to all buried water and gas lines
- Bends in ground wires must be made as close as possible to a right angle
- Lightning grounds must be connected to all ungrounded wiring
- They must be bonded together with all other grounds (correct answer)
Correct answer: D, They must be bonded together with all other grounds
Explanation
All ground rods and grounding systems at a site, including lightning, station and electrical service grounds, must be bonded together. If separate grounds are left unbonded, a strike can raise one to a very different voltage from another, and current can flash through equipment or people between them. Bonding keeps every ground at the same potential.
Why the other answers are wrong
- A, They must be bonded to all buried water and gas lines: Gas lines must not be used as part of a grounding system, and plastic or insulated buried pipes are not reliable ground paths.
- B, Bends in ground wires must be made as close as possible to a right angle: Sharp bends add inductance and invite arcing, so lightning ground conductors should run as straight as possible, with any bends gentle.
- C, Lightning grounds must be connected to all ungrounded wiring: Tying a lightning ground to ungrounded circuit conductors would short live wiring and could send strike energy into the circuits.