General Question G4C05
G4C: Interference to consumer electronics; grounding and bonding
What is a possible cause of high voltages that produce RF burns?
- Flat braid rather than round wire has been used for the ground wire
- Insulated wire has been used for the ground wire
- The ground rod is resonant
- The ground wire has high impedance on that frequency (correct answer)
Correct answer: D, The ground wire has high impedance on that frequency
Explanation
A ground wire is a transmission line at RF. If its length is near an odd multiple of a quarter wavelength, the low impedance at the ground rod is transformed to a high impedance at the equipment end. That leaves the chassis at a high RF voltage, so touching the radio, microphone or key can cause an RF burn.
Why the other answers are wrong
- A, Flat braid rather than round wire has been used for the ground wire: Flat braid or strap has lower RF inductance than round wire and is often preferred. It does not cause high voltages.
- B, Insulated wire has been used for the ground wire: Insulation on the ground wire has no effect on its RF impedance or the voltage at the station.
- C, The ground rod is resonant: The rod is driven into the earth and is not what resonates. The problem comes from the length of the wire between the station and the rod.