General Question G0B03
G0B: Station safety: electrical shock, grounding, fusing, interlocks, and wiring; antenna and tower safety
Which size of fuse or circuit breaker would be appropriate to use with a circuit that uses AWG number 14 wiring?
- 30 amperes
- 25 amperes
- 20 amperes
- 15 amperes (correct answer)
Correct answer: D, 15 amperes
Explanation
A fuse or breaker protects the wiring, so its rating must not exceed what the wire can safely carry. Under the NEC, AWG 14 copper is limited to a 15 A overcurrent device. Remember the pairs: AWG 14 with 15 A, AWG 12 with 20 A, AWG 10 with 30 A. A larger breaker would let the wire overheat before it tripped.
Why the other answers are wrong
- A, 30 amperes: 30 A is the rating for AWG 10 wire; on AWG 14 it would allow twice the safe current and create a fire risk.
- B, 25 amperes: 25 A exceeds what AWG 14 can safely carry, so the wire could overheat before the breaker opened.
- C, 20 amperes: 20 A is the rating for AWG 12 wire; AWG 14 is thinner and must be protected at 15 A.